Legislation
Construction Projects
O. Reg. 213/91Part II GENERAL CONSTRUCTION
Section 207
207. (1) If a built-up roof is being constructed, repaired or resurfaced, a barrier shall be placed in the immediate work area at least two metres from the perimeter of the roof.
(2) The barrier shall consist of portable weighted posts supporting a taut chain, cable or rope that is located 1.1 metres above the roof level.
Section 208
208. (1) A pipe that supplies hot tar or bitumen to a roof shall be securely fixed and supported to prevent its deflection.
(2) If a pipe discharges hot tar or bitumen two metres or less from the edge of a roof, a guardrail shall be provided at the edge of the roof.
[O. Reg. 142/17, s. 24]
Section 209
209. (1) A hoist used on a roof,
(a) shall have a guardrail installed on both sides of the frame at the edge of the roof; and
(b) shall be positioned in such a way that the hoist cable is vertical at all times while a load is being hoisted.
(2) Only a competent worker shall operate a hoist used on a roof.
Section 210
210. The counterweights on a roofer's hoist,
(a) shall be suitable for the purpose;
(b) shall not consist of roofing or other construction material;
(c) shall be securely attached to the hoist; and
(d) shall provide a safety factor against overturning of not less than three.