Legislation
Construction Projects
O. Reg. 213/91Part II GENERAL CONSTRUCTION
Section 41
41. A combustible, corrosive or toxic substance shall be stored in a suitable container.
Section 42
42. (1) A storage cylinder for compressed gas shall be secured in an upright position.
(2) The control valve of a storage cylinder for compressed gas, other than a cylinder connected to a regulator, supply line or hose, shall be covered by a protective cap that is secured in its proper position.
(3) A spent storage cylinder shall not be stored inside a building.
(4) No storage cylinder for propane shall be placed closer than three metres to a source of ignition or fire.
(5) Subsection (4) does not apply to a storage cylinder,
(a) that forms part of hand-held propane equipment;
(b) that forms part of a lead pot used in plumbing or electrical work;
(c) that forms part of a propane-powered or propane-heated vehicle; or
(d) that is protected from a source of ignition by a barrier, wall or other means of separation.
Section 43
43. (1) A flammable liquid or gas shall be stored in a building or storage tank that is suitable for the purpose and, if practicable, not less than 100 metres from a magazine for explosives.
(2) No more than one work day's normal supply of a flammable liquid shall be stored in a building or structure on a project unless it is stored,
(a) in a container that is suitable for the particular hazards of the liquid; and
(b) in a controlled access area or a room,
(i) that has sufficient window area to provide explosion relief to the outside, and
(ii) that is remote from the means of egress from the building or structure.
(3) A portable container used to store or transport flammable liquids,
(a) shall be approved for use for that liquid by a recognized testing laboratory; and
(b) shall have a label stating the use for which the container is approved and the name of the testing laboratory which gave the approval required by clause (a).
Section 211
211. (1) Only a competent worker shall operate a hot tar or bitumen road tanker or kettle.
(2) If a hot tar or bitumen road tanker or kettle is fitted with a propane-fuelled heater,
(a) the storage cylinder for propane shall not be placed closer than three metres to a source of fire or ignition;
(b) the lines connecting the storage cylinder for propane to the heating device shall be located so that they do not come into contact with the hot tar or bitumen in the case of a spill or a failure of a component of the system; and
(c) a fire extinguisher with an Underwriters' Laboratories of Canada rating of at least 4A40BC shall be provided with the road tanker or kettle.
(3) A propane burner used on a bitumen road tanker or kettle,
(a) shall have a thermal rating no greater than that recommended by the manufacturer of the road tanker or kettle; and
(b) shall consist of components that are adequate for their intended use.
(4) Hot tar or bitumen shall be transferred from a road tanker to a kettle through enclosed piping.