Legislation
Construction Projects
O. Reg. 213/91Part II GENERAL CONSTRUCTION
Section 181
181. (1) Except where otherwise required by this Regulation, electrical work performed on or near electrical transmission or distribution systems shall be performed in accordance with the document entitled "Electrical Utility Safety Rules" published by the Infrastructure Health and Safety Association and revised 2019.
(2) Sections 182, 187, 188, 189, 190, 191 and 193 do not apply to electrical work that is performed on or near electrical transmission or distribution systems if the work is performed in accordance with the document referred to in subsection (1).
[O. Reg. 631/94, s. 6; 627/05, s. 4; 443/09, s. 5; 345/15, s. 22; 327/19, s. 2]
Section 183
183. Every reasonable precaution shall be taken to prevent hazards to workers from energized electrical equipment, installations and conductors.
[O. Reg. 143/99, s. 1; 627/05, ss. 5, 6]
Section 190
190. (1) This section applies if work is to be done on or near energized exposed parts of electrical equipment or of an electrical installation or conductor.
(2) An employer shall,
(a) establish and implement written measures and procedures for complying with this section to ensure that workers are adequately protected from electrical shock and burn; and
(b) make a copy of the written measures and procedures available to every worker on the project.
(3) The worker shall follow the written measures and procedures.
(4) Subject to subsection (9), the power supply to the electrical equipment, installation or conductor shall be disconnected, locked out of service and tagged in accordance with subsection (6) before the work begins, and kept disconnected, locked out of service and tagged while the work continues.
(5) Hazardous stored electrical energy shall be adequately discharged or contained before the work begins and shall be kept discharged or contained while the work continues.
(6) The following rules apply to the tagging of the power supply under subsection (4):
1. The tag shall be made of non-conducting material and shall be installed so as not to become energized.
2. The tag shall be placed in a conspicuous location and shall be secured to prevent its inadvertent removal.
3. The tag shall indicate,
i. why the equipment, installation or conductor is disconnected,
ii. the name of the person who disconnected the equipment, installation or conductor,
iii. the name of the person's employer, and
iv. the date on which the equipment, installation or conductor was disconnected.
4. The tag shall not be removed unless it is safe to do so.
(7) A worker, before beginning work to which this section applies, shall verify that subsections (4) and (5) have been complied with.
(8) If more than one worker is involved in work to which this section applies, a means shall be provided to communicate the purpose and status of,
(a) the disconnecting, locking out and tagging of the electrical equipment, installation or conductor; and
(b) the discharging and containment of any hazardous stored electrical energy.
(9) Locking out is not required under subsection (4) if,
(a) in the case of a conductor, it is adequately grounded with a visible grounding mechanism;
(b) in the case of equipment or an installation,
(i) the power supply is less than 300 volts, the equipment or installation was not manufactured with provision for a locking device for the circuit breakers or fuses, and a written procedure has been implemented that is adequate to ensure that the circuit is not inadvertently energized, or
(ii) the power supply is 300 or more volts but not more than 600 volts, the equipment or installation was not manufactured with provision for a locking device for the circuit breakers or fuses, a written procedure as to how work is to be done has been implemented and the work is supervised by a competent worker to ensure that the circuit is not inadvertently energized.
[O. Reg. 627/05, s. 7]